Quote:
Originally Posted by deep_end
Bro,

I JUST knew it was too good to be true.

So, in general is the PF of 0.7 a conservative enough figure to work with, or is this limited to most pumps? And is 10% a reasonable power loss for an inverter?
depending .. there is no sure way of telling the power factor without actual measurement. Some pumps comes with a rated ampere so you may take reference from there. Resun MD55 is rated at 130watts but consumes ~0.8A.

If the pump does not come with the specs .. you may take it to have a power factor of 0.7 or lower. Its better to overdesign than underdesign.

10% power loss is reasonable for a good inverter .. again depending on the quality of it. May range from 10% to 30%
BarraCuda™ is offline   Reply With Quote
Old 01-01-2005, 10:11 PM   #22
cwloo
Guest
 
Posts: n/a
Default

Quote:
Originally Posted by BarraCuda™
then its not worth it anymore .. using a 270Ah battery will yield abt 3000VA .. much much more than 1000VA
oh .. didn't read the 270Ah ...
  Reply With Quote
Old 03-01-2005, 05:03 PM   #23
deep_end
Guest
 
Posts: n/a
Default

Bro,

Quote:
Originally Posted by BarraCuda™
depending .. there is no sure way of telling the power factor without actual measurement. Some pumps comes with a rated ampere so you may take reference from there. Resun MD55 is rated at 130watts but consumes ~0.8A.
so in this case, 0.8A = 192W (based on 240V), is this current draw more accurate than the pump consumption of 130W? If a clamp-meter is used, will it show amps or watts?

Quote:
Originally Posted by BarraCuda™
If the pump does not come with the specs .. you may take it to have a power factor of 0.7 or lower. Its better to overdesign than underdesign.

10% power loss is reasonable for a good inverter .. again depending on the quality of it. May range from 10% to 30%
Hmm, OK, gotcha, thanks.
  Reply With Quote
Old 03-01-2005, 05:53 PM   #24
cwloo
Guest
 
Posts: n/a
Default

Quote:
Originally Posted by deep_end
Bro,


so in this case, 0.8A = 192W (based on 240V), is this current draw more accurate than the pump consumption of 130W? If a clamp-meter is used, will it show amps or watts?


Hmm, OK, gotcha, thanks.
Yes, the current draw is 0.8A = 192w = apparent power (VA).
Higher because of the reactive power.
  Reply With Quote
Old 03-01-2005, 11:44 PM   #25
BarraCuda™
SiaoGu Gives You Wings
 
BarraCuda™'s Avatar
 
Join Date: Jul 2001
Posts: 4,169
Default

Quote:
Originally Posted by deep_end
Bro,


so in this case, 0.8A = 192W (based on 240V), is this current draw more accurate than the pump consumption of 130W? If a clamp-meter is used, will it show amps or watts?

cwloo is correct, the actual ampere drawn will be ~0.8A due to reactive power. Clampmeter will only show amperes/voltage.

I took a actual measurement of my resun MD55, its abt ~0.9A which is higher than the rated 0.8A.

So 0.9A X 240V = 216VA

Assuming the rated wattage is correct

130watts/216VA = powerfactor = 0.6
BarraCuda™ is offline   Reply With Quote
Old 04-01-2005, 06:35 PM   #26
deep_end
Guest
 
Posts: n/a
Default

That's not very efficient, is it?

I think not many people (like me) realize this. And think that 1 VA = 1 W. To certain extent, the specs on the label is a case of misrepresentation. As far as power consumption is concerned, we're only paying for the 130W and not the 216VA, right?
  Reply With Quote
Old 04-01-2005, 07:15 PM   #27
BarraCuda™
SiaoGu Gives You Wings
 
BarraCuda™'s Avatar
 
Join Date: Jul 2001
Posts: 4,169
Default

Quote:
Originally Posted by deep_end
That's not very efficient, is it?

I think not many people (like me) realize this. And think that 1 VA = 1 W. To certain extent, the specs on the label is a case of misrepresentation. As far as power consumption is concerned, we're only paying for the 130W and not the 216VA, right?
yes, we are only paying for the 130W if the its rated correctly. Now to drop another bomb .. the back pressure may have an effect on power consumption. Some pumps they publish load/wattage charts where it shows the actual power consumption under specific loads.

Now .. resun MD55 is rated at 130W but at what load? Max load? Min load? My guess is that the resun MD55 is rated at the max load/min wattage while iwaki is rated at min load/max wattage.

Taken from a post from Roidan in SRC


The power consumption of the pump increases when the flowrate is higher! Roidan measured a 0.95A for his MX100 while I got ~0.9A for my resun MD55? Fishy isnt it?

If I based on the rated 130watts and calculate the monthly kWh costs, it doesnt tally with the actual increased in electricity bills!

So now, we realised that using a pressure rated pump for non-pressure rated application isnt really a good thing. You got less flow per hr and get higher electrical bills!
BarraCuda™ is offline   Reply With Quote
Old 06-01-2005, 12:51 AM   #28
deep_end
Guest
 
Posts: n/a
Default

Ah so!!!! No wonder my electricity bill estimates never seem to tally with the real thing. Damn !!!
  Reply With Quote
Old 06-01-2005, 07:16 PM   #29
BarraCuda™
SiaoGu Gives You Wings
 
BarraCuda™'s Avatar
 
Join Date: Jul 2001
Posts: 4,169
Default

Renaming this thread to UPS and power consumption
BarraCuda™ is offline   Reply With Quote
Old 07-01-2005, 12:15 AM   #30
ReDDeviLs
Guest
 
Posts: n/a
Default

ah! time to get rid of my md55! but how about my beckett? alamak!
  Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT +9. The time now is 11:51 PM.


Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright © 2000-2008 Arofanatics.com (Since 30th August 2000)